Answer:
The temperature of the strip as it exits the furnace is 819.15 °C
Explanation:
The characteristic length of the strip is given by;

The Biot number is given as;

< 0.1, thus apply lumped system approximation to determine the constant time for the process;

The time for the heating process is given as;

Apply the lumped system approximation relation to determine the temperature of the strip as it exits the furnace;

Therefore, the temperature of the strip as it exits the furnace is 819.15 °C
Answer:
A) Sump pit
Explanation:
A wastewater typically refers to a body of water that has contaminated through human use in homes, offices, schools, businesses etc. Wastewater are meant to be disposed in accordance with the local regulations and standards because they are unhygienic for human consumption or use.
Generally, many homes use a floor drain in their bathrooms and toilets to remove wastewater in order to mitigate stagnation and to improve hygiene. A floor drain can be defined as a material installed on floors for the continuous removal of any stagnant wastewater in buildings. Wastewater flows into a sump pit once it is released into a floor drain through the use of a pipe such as a polyvinyl chloride (PVC) pipe, which directly connects the floor drain to the sump pit. The wastewater can the be removed from the sump pit when it is filled up through the use of a pump.
,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,,
Vlad [161]
Answer:
Explanation:
you need more information x
Answer:
it is not possible to place the wires in the condui
Explanation:
given data
total area = 2.04 square inches
wires total area = 0.93 square inches
maximum fill conduit = 40%
to find out
Can it is possible place wire in conduit conduit
solution
we know maximum fill is 40%
so here first we get total area of conduit that will be
total area of conduit = 40% × 2.04
total area of conduit = 0.816 square inches
but this area is less than required area of wire that is 0.93 square inches
so we can say it is not possible to place the wires in the conduit