Answer: P = 0.416 kW
Explanation:
taken a step by step process to solving this problem.
we have that from the question;
the amount of heat rejected Qn = 4800 kJ/h
the cooling effect is Ql = 3300 kJ/h
Applying the first law of thermodynamics for this system gives us
Шnet = Qn -Ql
Шnet = 4800 - 3300 = 1500 kJ/h
Next we would calculate the coefficient of performance of the refrigerator;
COPr = Desired Effect / work output = Ql / Шnet = 3300/1500 = 2.2
COPr = 2.2
The Power as required gives;
P = Qn - Ql = 4800 - 3300 = 1500 kJ/h = 0.416
P = 0.416 kW
cheers i hope this helps!!!!1
Location of the class depends on satiation
Answer:
The value of heat transferred watt per foot length Q = 54.78 Watt per foot length.
Explanation:
Diameter of pipe = 2 in = 0.0508 m
Steam temperature
= 300 F = 422.04 K
Duct temperature
= 70 F = 294.26 K
Emmisivity of surface 1 = 0.79
Emmisivity of surface 2 = 0.276
Net emmisivity of both surfaces ∈ = 0.25
Stefan volazman constant
= 5.67 ×

Heat transfer per foot length is given by
Q = ∈
A (
) ------ (1)
Put all the values in equation (1) , we get
Q = 0.25 × 5.67 ×
× 3.14 × 0.0508 × 1 × (
)
Q = 54.78 Watt per foot.
This is the value of heat transferred watt per foot length.
Answer:
The perceived economic impact of CO2 generated per year by lighting sstem is $8164.67.
Explanation:
The CO2 requirement for the plant is:
Amount of CO2 per year = (2.4 lb / KWh)(300,000 KWh)
Amount of CO2 per year = (720000 lb)(1 ton/ 2204.62 lb)
Amount of CO2 per year = 326.59 ton
The perceived economic impact of CO2 generated per year will then be:
Economic Impact = ($25 / ton)(326.59 ton)
<u>Economic Impact = $8164.67</u>