Answer:
it is not possible to place the wires in the condui
Explanation:
given data
total area = 2.04 square inches
wires total area = 0.93 square inches
maximum fill conduit = 40%
to find out
Can it is possible place wire in conduit conduit
solution
we know maximum fill is 40%
so here first we get total area of conduit that will be
total area of conduit = 40% × 2.04
total area of conduit = 0.816 square inches
but this area is less than required area of wire that is 0.93 square inches
so we can say it is not possible to place the wires in the conduit
Answer:
B- extreme fit, close fit, adjustable fit
Explanation:
A human-fit design typically involves the process of manufacturing or producing products (tools) that are easy to use by the end users. Therefore, human-fit designs mainly deals with creating ideas that makes the use of a particular product comfortable and convenient for the end users.
The design for human-fit strategies include; extreme fit, close fit and adjustable fit.
Hence, when the aforementioned strategies are properly integrated into a design process, it helps to ensure the ease of use of products and guarantees comfort for the end users.
OSHA inspections are generally unannounced. In fact, except in four exceptional circumstances when advance notice may be given.
It is a criminal offense for any person to give unauthorized advance notice of an OSHA inspection.
Answer:
78 MPa
Explanation:
Given that the critical resolved shear stress for a metal is 39 MPa, the maximum possible yield strength for a single crystal of this metal is twice the critical resolved shear stress for the metal. The maximum yield yield strength for a single crystal of this metal that is pulled in tension (
) is given as: