Answer:
the quality of the refrigerant exiting the expansion valve is 0.2337 = 23.37 %
Explanation:
given data
pressure p1 = 1.4 MPa = 14 bar
temperature t1 = 32°C
exit pressure = 0.08 MPa = 0.8 bar
to find out
the quality of the refrigerant exiting the expansion valve
solution
we know here refrigerant undergoes at throtting process so
h1 = h2
so by table A 14 at p1 = 14 bar
t1 ≤ Tsat
so we use equation here that is
h1 = hf(t1) = 332.17 kJ/kg
this value we get from table A13
so as h1 = h2
h1 = h(f2) + x(2) * h(fg2)
so
exit quality = 
exit quality = 
so exit quality = 0.2337 = 23.37 %
the quality of the refrigerant exiting the expansion valve is 0.2337 = 23.37 %
Answer:
the elevation at point X is 2152.72 ft
Explanation:
given data
elev = 2156.77 ft
BS = 2.67 ft
FS = 6.72 ft
solution
first we get here height of instrument that is
H.I = elev + BS ..............1
put here value
H.I = 2156.77 ft + 2.67 ft
H.I = 2159.44 ft
and
Elevation at point (x) will be
point (x) = H.I - FS .............2
point (x) = 2159.44 ft - 6.72 ft
point (x) = 2152.72 ft