Answer:
There is 0.466 KW required to operate this air-conditioning system
Explanation:
<u>Step 1:</u> Data given
Heat transfer rate of the house = Ql = 755 kJ/min
House temperature = Th = 24°C = 24 +273 = 297 Kelvin
Outdoor temperature = To = 35 °C = 35 + 273 = 308 Kelvin
<u>Step 2: </u> Calculate the coefficient of performance o reversed carnot air-conditioner working between the specified temperature limits.
COPr,c = 1 / ((To/Th) - 1)
COPr,c = 1 /(( 308/297) - 1)
COPr,c = 1/ 0.037
COPr,c = 27
<u>Step 3:</u> The power input cna be given as followed:
Wnet,in = Ql / COPr,max
Wnet, in = 755 / 27
Wnet,in = 27.963 kJ/min
Win = 27.963 * 1 KW/60kJ/min = 0.466 KW
There is 0.466 KW required to operate this air-conditioning system
Answer:
I am Providing Answer in C Language Program.
Explanation:
Please find attachment regarding code of taking two numbers input and adding them.
I would like to recommend you please use software which supports C language.
#include <stdio.h>
int main () {
int a, b, sum;
printf ("\ nEnter two no:");
scanf ("% d% d", & d, & e);
sum1 = d + e;
printf ("Sum:% d", sum1);
return (0);
}
Answer:
Evaporator,Compressor,Condensor ,Expanding valve
Explanation:
Split air conditioning :
Split air conditioning means that, condensor unit or some time called outdoor unit is split from evaporator.It means that evaporator and condensor are placed at some distance.
The four component of split air conditioning system are as follows
1.Evaporator
It absorb heat from room and produces the cooling effect.
2.Compressor
It compresses the refrigerant which exits from evaporator.
3.Condensor
It rejects the heat and cool the evaporator.
4.Expanding valve
It allows to refrigerant to cool up to evaporator pressure.
Answer:
the heat transfer from the pipe will decrease when the insulation is taken off for r₂< ![r_{cr}](https://tex.z-dn.net/?f=r_%7Bcr%7D)
where;
r₂ = outer radius
= critical radius
Explanation:
Note that the critical radius of insulation depends on the thermal conductivity of the insulation k and the external convection heat transfer coefficient h .
![r_{cr} =\frac{k}{h}](https://tex.z-dn.net/?f=r_%7Bcr%7D%20%3D%5Cfrac%7Bk%7D%7Bh%7D)
The rate of heat transfer from the cylinder increases with the addition of insulation for outer radius less than critical radius (r₂<
) 0, and reaches a maximum when r₂ =
, and starts to decrease for r₂<
. Thus, insulating the pipe may actually increase the rate of heat transfer from the pipe instead of decreasing it when r₂<
.