Answer:
Option A, B and D
Explanation:
Jack can easily convince boss if he focus around two major aspects of the company
a) Revenue enhancement - Jack must outline the benefits of his research that can be used to improvise customer offerings and hence can be further used to devise more energy-efficient options to customer
b) Reduction in mistakes - Issues such as poor implementation can be avoided with better approach and understanding.
Hence, option A, B and D are correct
Answer:
There 11,238,513 different Powerball
Answer:
a mass of water required is mw= 1273.26 gr = 1.27376 Kg
Explanation:
Assuming that the steam also gives out latent heat, the heat provided should be same for cooling the hot water than cooling the steam and condense it completely:
Q = mw * cw * ΔTw = ms * cs * ΔTw + ms * L
where m = mass , c= specific heat , ΔT=temperature change, L = latent heat of condensation
therefore
mw = ( ms * cs * ΔTw + ms * L )/ (cw * ΔTw )
replacing values
mw = [182g * 2.078 J/g°C*(118°C-100°C) + 118 g * 2260 J/g ] /[4.187 J/g°C * (90.7°C-39.4°C)] = 1273.26 gr = 1.27376 Kg
Answer:
Electrical energy is energy derived as a result of movement of electrons. When used loosely, electrical energy refers to energy that has been converted from electric potential energy. ... Once converted from potential energy, electrical energy can always be called another type of energy (heat, light, motion, etc.)
Explanation:
<h2><em>hope</em><em> </em><em>it</em><em> </em><em>is</em><em> </em><em>helpful</em><em> </em><em>for</em><em> </em><em>you</em><em> </em></h2><h2><em>keep</em><em> </em><em>smiling</em><em> </em></h2>
Answer:
a. 2.08, b. 1110 kJ/min
Explanation:
The power consumption and the cooling rate of an air conditioner are given. The COP or Coefficient of Performance and the rate of heat rejection are to be determined. <u>Assume that the air conditioner operates steadily.</u>
a. The coefficient of performance of the air conditioner (refrigerator) is determined from its definition, which is
COP(r) = Q(L)/W(net in), where Q(L) is the rate of heat removed and W(net in) is the work done to remove said heat
COP(r) = (750 kJ/min/6 kW) x (1 kW/60kJ/min) = 2.08
The COP of this air conditioner is 2.08.
b. The rate of heat discharged to the outside air is determined from the energy balance.
Q(H) = Q(L) + W(net in)
Q(H) = 750 kJ/min + 6 x 60 kJ/min = 1110 kJ/min
The rate of heat transfer to the outside air is 1110 kJ for every minute.