Answer: D) All of the above
Explanation:
Burn rate can be affected by all of the above reasons as, variation in chamber pressure because the pressure are dependence on the burn rate and temperature variation in initial gain can affect the rate of the chemical reactions and initial gain in the temperature increased the burning rate. As, gas flow velocity also influenced to increasing the burn rate as it flowing parallel to the surface burning. Burn rate is also known as erosive burning because of the variation in flow velocity and chamber pressure.
Answer:
Yes
Explanation:
Yes it is true that COP of heat pump always greater than 1.But the COP of refrigeration can be greater or less than 1.
We know that
COP of heat pump= 1 + COP of refrigeration
It is clear that COP can not be negative .So from the above expression we can say that COP of heat pump is always greater than one.
Answer:
COP of the heat pump is 3.013
OP of the cycle is 1.124
Explanation:
W = Q₂ - Q₁
Given
a)
Q₂ = Q₁ + W
= 15 + 7.45
= 22.45 kw
COP = Q₂ / W = 22.45 / 7.45 = 3.013
b)
Q₂ = 15 x 1.055 = 15.825 kw
therefore,
Q₁ = Q₂ - W
Q₁ = 15.825 - 7.45 = 8.375
∴ COP = Q₁ / W = 8.375 / 7.45 = 1.124
Answer:
Im guessing this is for CEA for PLTW, if so look up the exact assignment number and look at online examples of the exact same assignment.
Explanation:
Same question idea but different values... I hope I helped you... Don't forget to put a heart mark