Using the characteristics equation, determine the dynamic behavior of a PI controller with τI = 4 applied to a second order proc

ess (Kp = 2, τn = 5 and ζ = 1.5). Assume that Gc(s) and Ga(s) are equal to unity. Find the values of Kc that render this closed-loop process unstable.
Characteristic Equaton : Gp*Ga*Gc*Gs + 1 = 0
Engineering
1 answer:
Sladkaya [172]3 years ago
8 0

Answer:

The values of Kc that render this closed-loop process unstable are in the interval

(Kc < 0)

Explanation:

The transfer function of a PI controller is given as

Gc = Kc {1 + (1/sτI)}

τI = 4

Gc = Kc {1 + (1/4s)}

Gc = Kc {(4s+1)/(4s)}

Divide numerator and denominator by 4

Gc = Kc {(s+0.25)/(s)}

For a second order process, the general transfer function is given by

Gp = Kp {1/(τn²s² + 2ζτns + 1)}

Kp = 2, τn = 5 and ζ = 1.5

Gp = 2/(25s² + 15s + 1)

Divide numerator and denominator by 25

Gp = 0.08/(s² + 0.6s + 0.04)

Ga = 1

Gs = 1

We need to find the value(s) of Kc that makes the closed loop transfer function unstable. Gp*Ga*Gc*Gs + 1 = 0

The closed loop transfer function is unstable when the solution(s) of the characteristic equation obtained is positive.

Gp*Ga*Gc*Gs + 1 = 0

Becomes

[0.08/(s² + 0.6s + 0.04)] × [Kc (s+0.25)/(s)] + 1 = 0

[0.08Kc (s + 0.25)/(s³ + 0.6s² + 0.04s)] = - 1

0.08Kc (s + 0.25) = -s³ - 0.6s² - 0.04s

0.08Kc s + 0.02Kc = -s³ - 0.6s² - 0.04s

s³ + 0.6s² + 0.04s + 0.08Kc s + 0.02Kc = 0

s³ + 0.6s² + (0.08Kc + 0.04)s + 0.02Kc = 0

We will use the direct substitution method to evaluate the values of Kc that matter. The values of Kc at the turning points of the closed loop transfer function.

For the substitution,

We put s = jw into the equation. (frequency analysis)

Note that j = √(-1)

s³ + 0.6s² + (0.08Kc + 0.04)s + 0.02Kc = 0

(jw)³ + 0.6(jw)² + (0.08Kc + 0.04)(jw) + 0.02Kc = 0

-jw³ - 0.6w² + (0.08Kc + 0.04)(jw) + 0.02Kc = 0

we then collect terms with j and terms without.

(0.08Kcw + 0.04w - w³)j + (0.02Kc - 0.6w²) = 0

Meaning,

0.08Kcw + 0.04w - w³ = 0 (eqn 1)

0.02Kc - 0.6w² = 0 (eqn 2)

0.02 Kc = 0.6 w²

Kc = 15w²

Substituting this into eqn 1

0.08Kcw + 0.04w - w³ = 0

Kc = 15w²

0.08(15w²)w + 0.04w - w³ = 0

1.2w³ + 0.04w - w³ = 0

0.2w³ + 0.04w = 0

w = 0 or 0.2w² + 0.04 = 0

0.2w² = -0.04

w² = -0.2

w = ± √(-0.2)

w = ± 0.4472j or w = 0

Recall, Kc = 15w² = 15(-0.2) = -3 or Kc = 0

The turning points for the curve of the closed loop transfer function occur when

Kc = 0 or Kc = -3

To investigate, we pick values around these turning points to investigate the behaviour of the closed loop transfer function at those points.

Kc < -3, Kc = -3, (-3 < Kc < 0), Kc = 0 and Kc > 0

Note that, one positive characteristic root or pole is enough to make the system unstable.

We pick a value for Kc in that interval and evaluate the closed loop transfer function.

s³ + 0.6s² + (0.08Kc + 0.04)s + 0.02Kc = 0

- First of, let Kc = - 4 (Kc < -3)

s³ + 0.6s² - 0.28s - 0.08 = 0

Solving the polynomial

s = (-0.22002), 0.44223, (-0.82221)

One positive pole means the closed loop transfer function is unstable in this region

Let Kc = -3

s³ + 0.6s² - 0.20s - 0.06 = 0

s = 0.37183, (-0.21251) or (-0.75933)

One positive pole still means that the closed loop transfer function is still unstable.

Then the next interval

Let Kc = -1

s³ + 0.6s² - 0.04s - 0.02 = 0

Solving this polynomial,

s = 0.18686, (-0.1749) or (-0.61196)

The function is unstable in the region being investigated.

Let Kc = 0

s³ + 0.6s² + 0.04s = 0

s = 0, -0.0769, -0.5236

One zero, all negative roots, indicate that the closed loop transfer function is marginally stable at this point.

Let Kc = 1, Kc > 0

s³ + 0.6s² + 0.12s + 0.02 = 0

s = (-0.42894), (-0.08553 + 0.1983j) or (-0.08553 - 0.1983j)

All the real negative parts of the poles are all negative, this indicates stability.

Hence, after examining the turning points of the closed loop transfer function, it is evident that, the region's of Kc where the closed loop transfer function is unstable is (Kc < 0)

Hope this Helps!!!

You might be interested in
Discuss the differences between conduction and convective heat transfer.
FrozenT [24]

Answer:

Basically there are two principal differences between the convection and conduction heat transfer

Explanation:

The conduction heat transfer is referred to the transfer between two solids due a temperature difference, while for, the convective heat transfer is referred to the transfer between a fluid (liquid or gas) and a solid. Also, they used different coefficients for its calculation.

We can include on the explanation that conduction thermal transfer is due to temperature difference, while convection thermal transfer is due to density difference.

8 0
2 years ago
Technician A says you should place the air ratchet setting to
Bas_tet [7]
I think it’s b sry if I’m wrong tho
6 0
2 years ago
The first step in treating shock is to
san4es73 [151]

Answer:

Lay the person down and elevate thier legs slightly.

Explanation:

5 0
2 years ago
Ruler game, HELPPPPP
viktelen [127]
D! :D
Hope I helped!!
3 0
2 years ago
Read 2 more answers
If a pilot-operated check valve (POC) does not check flow, you will see a. erratic actuator movement b, no actuator movement c.
Volgvan

If a pilot-operated check valve (POC) does not check flow, you will see a. erratic actuator movement.

<h3>What is a pilot-operated check valve (POC)?</h3>

Pilot operated test valves paintings through permitting loose float from the inlet port via the opening port. Supplying a pilot strain to the pilot port permits float withinside the contrary direction. Air strain on pinnacle of the poppet meeting opens the seal permitting air to float freely.

An actuator fault is a form of failure affecting the machine inputs. Due to strange operation or fabric aging, actuator faults might also additionally arise withinside the machine. An actuator may be represented through additive and/or multiplicative fault.

Read more about the pilot-operated check valve:

brainly.com/question/13001928

#SPJ1

7 0
1 year ago
Other questions:
  • 1. Consider a city of 10 square kilometers. A macro cellular system design divides the city up into square cells of 1 square kil
    10·1 answer
  • Technician A says a basic circuit problem can be caused by something in the circuit that increases voltage. Technician B says a
    8·1 answer
  • Is a 68.75 and a 70 a pass in 5th grade?
    10·2 answers
  • The Bureau of Labor and Statistics predicted that the field of biomedical engineering would increase by 62 percent over the comi
    10·1 answer
  • Draw an ERD for each of the following situations. (If you believe that you need to make additional assumptions, clearly state th
    15·1 answer
  • 1. What are the usual symptoms of brake issues?​
    15·1 answer
  • Thermosets burn upon heating. a)-True b)- false?
    10·1 answer
  • Ten dollars per hour is about how much income per year
    5·2 answers
  • Find the remaining trigonometric functions of 0 if
    10·1 answer
  • To prevent drainage of the transmission fluid from the converter when the
    12·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!