The MCB of a rupas room is tripped and keeps on tripping again and again, and if it is a domestic circuit, what could be the reason for this phenomenon?
The reason could be a short circuit which is resulting in higher level of currents to pass through the MCB which is resulting in trip every time.
OR
The MCB is faulty and might need a replacement.
To Diagnose the problem further more.
Turn off all the switches in rupas room and then try turning on the MCB. If it trips again then MCB is faulty (Subjective to the fact there everything was normal before this issue and no signs of short circuit or spark in wiring were observed)
If MCB does not trip in point 1 then Turn ON all the switches one by one. This shall give you the cause of problem.
If their are choices you should list them. The givens are pretty specific though.
W = E * I is the answer
E (voltage) = W/I is a more refined answer. <<< answer.
Answer:
showm
Explanation:
Consider a dipole having magnetic moment 'm' is placed in magnetic field
then the torque exerted by the field on the dipole is


Now to rotate the dipole in the field to its final position the work required to be done is




Minimum energy mB is for the case when m is anti parallel to B.
Minimum energy -mB is for the case when m is parallel to B.
Answer:
Hans Lipperhey
....................................
Answer:
0.02585 BTU
Explanation:
Given: Spring constant, k = 270 lbf/in
Initial force, f =100 lbf
Compression, x = 1 in
Work done can be calculated as follows:
