Refrigerant 134a enters a horizontal pipe operating at steady state at 40°C, 300 kPa, and a velocity of 25 m/s. At the exit, the

temperature is 90°C and the pressure is 240 kPa. The pipe diameter is 0.1 m. Determine: (a) the mass flow rate of the refrigerant, in kg/s, (b) the velocity at the exit, in m/s, and (c) the rate of heat transfer between the pipe and its surroundings, in kW.
Engineering
1 answer:
salantis [7]3 years ago
3 0

Answer:

a) 2.42 kg/s

b) 37.20 m/s

c) 120.56 kW

Explanation:

Given that:

The fluid in the Refrigerant = R-134a

Diameter (d) = 0.1 m

In the Inlet:

Temperature T_1 = 40^0C

Pressure P_1= 300kPa

Velocity V_1 = 25 m/s

At the exit:

Temperature T_2 = 90^0C

Pressure P_2 = 240 kPa

From the  Table A-12 for Refrigerant R-134a at T_1 = 40^0C and P_1= 300kPa

Specific Volume v_1 = 0.0809 m^3/kg

From the  Table A-12 for Refrigerant R-134a at T_2 = 90^0C and P_2 = 240 kPa

Specific Volume v_2 = 0.12038 kJ/kg

Their corresponding Enthalpy h_1 and h_2 are as follows:

Enthalpy h_1  =284.05 kJ/kg

Enthalpy h_2 = 333 kJ/kg

a) The mass flow rate of the refrigerant can be calculated as :

m_1 = \frac{AV_1}{v_1}

m_1 = \frac{\frac{\pi (0.1)^2}{4}*25}{0.08089}

m_1 = 2.42 kg/s

b) The velocity at the exit point:

we knew that:

m=m_1 =m_2

∴

\frac{AV_1}{v_1} =\frac{AV_2}{v_2}

V_2 = \frac{v_2}{v_1} V_1

V_2 = \frac{0.12038}{0.08089} *25

V_2 = 37.20 m/s

c) Expression for calculating heat transfer (as long as there is no work that is said to be done and the pipe is horizontal) can be represented as:

Q_{cv}= m[(h_2-h_1)+\frac{1}{2}(V_2^2-V_1^2)]

Q_{cv}= 2.42*[(333.49-284.05)+\frac{1}{2}(37.20^2-25^2)]

Q_{cv}= 2.42*[49.44+379.42]

Q_{cv}= 119.6448kW+918.19W(\frac{1kW}{1000W} )

Q_{cv}= 119.6448kW+0.92 kW

Q_{cv} = 120.56 kW

You might be interested in
What is the volume of the rectangular prism shown.
Likurg_2 [28]
It would be 72cm bc u need to add up all the line in the back to
7 0
3 years ago
A vacuum gage connected to a tank reads 30 kPa at a location where the barometric reading is 755 mmHg. Determine the absolute pr
navik [9.2K]

Answer:

Absolute pressure=70.72 KPa

Explanation:

Given that Vacuum gauge pressure= 30 KPa

Barometer reading =755 mm Hg

We know that barometer always reads atmospheric pressure at given situation.So  atmospheric pressure is equal to  755 mm Hg.

We know that P= ρ g h

Density of Hg=13600 \frac{kg}{m^3}

So P=13600 x 9.81 x 0.755

P=100.72 KPa

We know that

Absolute pressure=atmospheric pressure + gauge pressure

But here given that 30 KPa is a Vacuum pressure ,so we will take it as negative.

Absolute pressure=atmospheric pressure + gauge pressure

Absolute pressure=100.72 - 30   KPa

So

Absolute pressure=70.72 KPa

8 0
3 years ago
100 kg of R-134a at 200 kPa are contained in a piston–cylinder device whose volume is 12.322 m3. The piston is now moved until t
LekaFEV [45]

Answer:

T=151 K, U=-1.848*10^6J

Explanation:

The given process occurs when the pressure is constant. Given gas follows the Ideal Gas Law:

 pV=nRT

For the given scenario, we operate with the amount of the gas- n- calculated in moles. To find n, we use molar mass: M=102 g/mol.  

Using the given mass m, molar mass M, we can get the following equation:  

 pV=mRT/M

To calculate change in the internal energy, we need to know initial and final temperatures. We can calculate both temperatures as:

T=pVM/(Rm); so initial T=302.61K and final T=151.289K

 

Now we can calculate change of U:

U=3/2 mRT/M using T- difference in temperatures

 U=-1.848*10^6 J

Note, that the energy was taken away from the system.  

5 0
3 years ago
One of the disadvantages of the test of the hypothesis is that the final decision cannot be said to be completely correct eviden
vfiekz [6]

Answer:

A. True

Explanation:

4 0
3 years ago
State five applications of thermochromic materials
rusak2 [61]

Explanation:

The end-use industries of thermochromic materials include packaging, printing & coating, medical, textile, industrial, and others. Printing & coating is the fastest-growing end-use industry of thermochromic materials owing to a significant increase in the demand for thermal paper for POS systems. The use of thermochromic materials is gaining momentum for interactive packaging that encourages consumers to take a product off the shelf and use it.

8 0
3 years ago
Other questions:
  • To unload a bound stack of plywood from a truck, the driver first tilts the bed of the truck and then accelerates from rest. Kno
    7·1 answer
  • The working section of a transonic wind tunnel has a cross-sectional area 0.5 m2. Upstream, where the cross-section area is 2 m2
    10·1 answer
  • Two hemispherical shells of inner diameter 1m are joined together with 12 equally spaced bolts. If the interior pressure is rais
    15·1 answer
  • 1. A fixed-geometry supersonic inlet starts at a Mach number of 3. After starting, the cruise Mach number is 2, and the operatin
    13·1 answer
  • Will this airplane stay in the air a long time? Why or why not?
    9·1 answer
  • Compute the thermal efficiency for an ideal gas turbine cycle that operates with a pressure ratio of 6.75 and uses helium gas.
    12·1 answer
  • Suggest how the following requirements might be rewritten in a
    8·1 answer
  • The hydraulic tool holder is a type of what? A.port B. clamp C. Press D. Actuator​
    11·1 answer
  • 8. Block A shown in the figure below weighs 2000 N. The chord attached to A passes over a
    9·1 answer
  • s) Use Cramer’s rule to solve the system below, and state the condition at which solution exists. ax+by = 1 cx+dy =−1
    15·1 answer
Add answer
Login
Not registered? Fast signup
Signup
Login Signup
Ask question!