Answer:
Hello your question has some missing information below are the missing information
The refrigerant enters the compressor as saturated vapor at 140kPa Determine The coefficient of performance of this heat pump
answer : 2.49
Explanation:
For vapor-compression refrigeration cycle
P1 = P4 ; P1 = 140 kPa
P2( pressure at inlet ) = P3 ( pressure at outlet ) ; P2 = 800 kPa
<u>From pressure table of R 134a refrigerant</u>
h1 ( enthalpy of saturated vapor at 140kPa ) = 239.16 kJ/kg
h2 ( enthalpy of saturated liquid at P2 = 800 kPa and t = 60°C )
= 296.8kJ/kg
h3 ( enthalpy of saturated liquid at P3 = 800 kPa ) = 95.47 kJ/kg
also h4 = 95.47 kJ/kg
To determine the coefficient of performance
Cop = ( h1 - h4 ) / ( h2 - h1 )
∴ Cop = 2.49
Answer:
C). rearview mirror (at least of four inches by four inches).
Explanation:
<u>A 'rearview mirror' would be needed in case one is required to pull an individual on water skis after a PWC(personal watercraft) that is rated for carrying two persons only</u>. This wide-angle mirror for rearview would allow the operator to monitor the person who is being towed constantly along with riding the ski at the same time. It is considered illegal to tow a person on a vessel without having a rearview mirror and at the same time, the limited capacity must also be followed strictly. Hence, <u>option C</u> is the correct answer.
Answer:
option c is correct
47.2%
Explanation:
given data
consisting of refrigerant = 134 a
volume V = 0.01 m³/kg
pressure P = 1MPa = 1000 kPa
to find out
quality of the R 134a
solution
we will get here value of volume Vf and Vv from pressure table 60 kpa to 3 Mpa for 1 Mpa of R134 a
that is
Vf = 0.0008701 m³/kg
Vv = 0.0203 m³/kg
so we will apply here formula that is
quality = (V - Vf) / (Vv - Vf) ............1
put here value
quality = (0.01 - 0.0008701 ) / ( 0.0203 - 0.0008701 )
quality = 0.4698
so quality is 47 %
SO OPTION C IS CORRECT