Answer:
114.26
Explanation:
a)Formula for per unit impedance for change of base is
Zpu2= Zpu1×(kV1/kV2)²×(kVA2/kVA1)
Zpu2: New per unit impedance
Zpu1: given per unit impedance
kV1: give base voltage
kV2: New bas votlage
kVA1: given bas power
kVA2: new base power
In the question
Zpu2=??
Zpu1= 0.3
kV2=24kV
kV1= 13.8 kV
kVA2= 1MVA ×1000= 1000 kVA
kVA1=500kVA
Zpu2= 0.3(13.8/24)²×(1000/500)
Zpu2= 0.198
b) to find ohmic impedance we will first calculate base value of impedance(Zbase). So,
Zbase= kV²/MVA
Zbase= 13.8²/(500/1000)
Zbase=380.88
Now that we have base value of impedance, Zbase, we can calculate actual ohmic value of impedance(Zactual) by using the following formula:
Zpu=Zactual/Zbase
0.3= Zactual/380.88
Zactual= 114.26 ohms
I’m 95% sure it’s covalent bonds.
The answer is B. This form of magnesium chloride is not a liquid but a solid that is white and colorless.
Answer:
c. Line - voltage thermostats and controls are not as sensitive as low - voltage thermostats.
Explanation:
Line voltage thermostat is a regulator which senses the temperature and maintains it to keep the desired level of the voltage. The license in required for the electricians to work on the voltage control wirings. There is technical aspects which an electrician must understand before working on the circuits and voltage lines.